S6-EH3P: grouped reads 33161–33189 and 44100–44112 cause intermittent Modbus timeouts #498
januszkadziela-lab
started this conversation in
General
Replies: 0 comments
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
Uh oh!
There was an error while loading. Please reload this page.
Setup
Problem
With normal cyclic polling enabled, the integration intermittently reports:
Network connectivity to the gateway is stable. A 300-packet ping test showed no packet loss, and TCP port 502 remains reachable.
Manual register tests
This suggests two separate grouped-read compatibility issues:
resolves the timeout.
Local workaround tested successfully
After these changes, cyclic polling and automations run without Modbus errors.
Request
Could the integration:
I can provide logs and exact register responses if needed.