Thanks again for raising this — I’ve now tested the Force Discharging route on the live system and you were right.

With PredBat requesting 8,000 W, Force Discharging made the battery output follow that battery-side request, while the resulting grid export varied according to the house load and PV. That matches PredBat’s discharge-rate model much more closely than Force Export, which was treating the requested value as the grid-export target and compensating for the load.

I’ve therefore updated the example to use AlphaESS Force Discharging for discharge_start_service. PredBat’s {target_soc} is now written directly to the Force Discharging stop-at-SOC control, with no added percentage offse…