Setting the loss % variables accurately #779
pacemaker82
started this conversation in
General
Replies: 2 comments 1 reply
|
I don't think the calculation is quite that simple, firstly make sure you have hybrid turned off. Then using the calibration chart look at the real charging rate vs the predicted one (e.g h8 vs actual) if the slope on the curves align then you are about right. If the predicted charges faster than reality then you should add more losses. I would guess inverter loss of 7% maybe closer to reality for AC coupled but I'd be interested to see your findings. |
0 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment



Uh oh!
There was an error while loading. Please reload this page.
Uh oh!
There was an error while loading. Please reload this page.
I need help setting up my battery charge/discharge loss %, as well as inverter loss %. These are the current settings, as installed.
I have an GivEnergy AC3 with 9.5kWh battery
input_number.predbat_battery_lossset to 3%input_number.predbat_battery_loss_dischargeset to 3%input_number.predbat_inverter_lossset to 4%I dont think these are right for my system, but need help in setting the right % in the right places. Looking at my discharge data for a full discharge during the night - my battery pushes out 3300w, 2600w going to grid, 200w going to house as base load. Thats a 500w loss ~16% from 3100w discharge to 2600w to grid.
If I am interpreting the settings above correctly, the discharge loss + inverter loss variables should equal ~16% ?(vs the 7% it currently has set)?
If so, what balance is discharge loss vs inverter loss?
FWIW 16% seems really high, but maybe I have incorrect expectations or approaching the calculations wrong